Run a 14/3 wire (you have to pull a wire anyway). Come into a 2 gang switch so if you don't need all the lights don't turn them on. Use the red wire for lights and the black wire for the outlets and the common neutral. Install a 2 pole 15 amp breaker in the panel. 2 circuits and you are working with your lighter wire. Come out of the 2 gang switch with 14/2.
It's 220/240v if the hot legs are coming off opposite bus bars in the panel. Otherwise they are just two legs of 110/120v operating in parallel. It would be absolutely no different that connecting 2 wires to a single pole 110/120v wire; they are both supplied by the same line in parallel. Electrical currents work in sine waves. 220v on opposite busses are opposite sine waves. The amperage through the lines is determined by the breaker, not by the amount of wiring.
Wiring a split wire circuit such as you're talking about is completely illegal. The red and the black must be hooked to opposite phases in the panelThe problem is this post. We're talking about two 15A circuits off a double breaker on the same pole. Two 15A breakers supplying power to two 14 gauge supply wires (one black one red in the 14-3). You are then expecting a single 14 gauge (white wire in the 14-3) to return a potential of 30A from the two breakers ON THE SAME POLE so double the 110V NOT two opposing sin wave 110V opposite circuits yielding 220V and no return on neutral.
Wiring a split wire circuit such as you're talking about is completely illegal. The red and the black must be hooked to opposite phases in the panel
I see now, sorry I missed that part.Correct but look at my post just previously. It was advised to supply those two 14ga wires with two breakers to double the allowed amperage. This is absolutely correct that the breaker determines the amount of amperage allowed to pass. That's exactly the problem we are allowing double the amount that neutral should be protected for.
I see now, sorry I missed that part.
Running unbalanced is a definite no. That's asking for trouble.
Thanks for clarifying that.
Could the OP go from panel to outlet branch, then at the end of the line of outlets supply the switch box for either a 2-way or 3-way light circuit? That way he would not need separate circuits for lights and outlets and could save the money from setting another home-run. All presuming that the design is calculated for load correctly, per code in his area.The -3 wire (14-3, 12-3, 10-3, etc) is used for 220v (two opposing legs in a single phase application) as Bill keeps bringing up or as travelers for a 3 way (or 4 way, etc) switch circuit. NOT to cheat physics and breakers to save on wire.
Could the OP go from panel to outlet branch, then at the end of the line of outlets supply the switch box for either a 2-way or 3-way light circuit? That way he would not need separate circuits for lights and outlets and could save the money from setting another home-run. All presuming that the design is calculated for load correctly, per code in his area.
That's what I thought. ThanksYes as long as all the wire is 12ga. You can not step down to 14ga on the 20A breaker even though the lights only use 1.2A and there is no way to plug in anything else, the wire would not be protected.